My question is we have a maximum of 247 slave IDs .
Each Device has some unique slave Id .
In this way can we connect only 247 different types of devices to the modbus . ?
Can i have some clear explaination please?
Solved! Go to Solution.
08-22-2011 01:11 AM
Hi,
Modbus is restricted to addressing 247 devices on one data link, which limits the number of field devices that may be connected to a master station.
However, if you want to increase the number of slaves, you may use MODBUS/TCP.
Here is a link that might help you:
http://modbus.control.com/thread/1026247380.
The Schneider electric 174CEV30010 Modbus to Ethernet bridge is capable of addressing Modbus slaves from 1 to 247.
The actual number of devices which can be physically connected depends on the medium used and not on the fact it is Modbus.
Some examples:
RS232 is a 2 device point to point connection when using copper, however when using fiber (or other modems) it is possible to connect up to the maximum of 247 devices.
RS485 is multi-drop and supports 32 devices on a single network. When a repeater is used, on copper wire, the number of devices can usually be increased to 64.