SP7 Error 6015 reading/writing DB string array

I am attempting to read and write a string array from a Siemens S7 1500 PLC. I have set up two different data blocks for these operations, one for reading and one for writing. But neither operation succeeds.

 

All other data blocks are reading and writing correctly ( Bools and Reals ) so I know it's not a problem accessing the PLC data in general.

 

All attempts to read or write, even trying to retrieve or send just one Item, fail with Error 6015: Data not valid! The data address exceeds the address range 

 

This happens whether I use the default 254 character strings or work with shorter strings.

 

I can find no examples on the 'net that explain any pitfalls with this operation.

 

Attached is an image of a simple test program for the read operation of a readable DB along with the VI. I don't think the Labview program structure is the problem, since it works fine for reading other data types.

 

There seems to be some subtle nuance to reading string arrays that I am not understanding. Or, the SP7 toolkit's ReadDB and WriteDB aren't handling the string arrays properly

 

Any suggestions are appreciated.

 

 

 

 

Download All
0 Kudos
Message 1 of 2
(807 Views)

The answer to this was a PLC programming error. The SP7 manual states:

 

DB´s have to be global accessible and the offset has to be static (“Optimize db lock access” unchecked)

 

The programmer had failed to turn off the optimization.

 

 

 

0 Kudos