DATA AHEAD toolkit support Discussions

cancel
Showing results for 
Search instead for 
Did you mean: 

SP7: SP7 open (connect.vi) Error 66

Hello,

I tried to optimize my sample rate.

I the first step of my state mashine i try to open the connection to the PLC S7-1200.

I feed the SP7 open block with the plc-Type (s7-1200 = 2), timeout =5000ms, Rack =2 and IP adress = 192.168.1.39

My plc type CPU1215F DC/DC/DC produces always the Error 66.

Why? And does somebody knows a solution?

 

regards

Raabun

0 Kudos
Message 1 of 3
(4,205 Views)
Please check the settings of the Ethernet port of your PLC in TIA portal. Explanation for error 66 is "Connection closed by the peer" hence it seems that the PLC is refusing the connection made by LabVIEW.

Regards,
DATA AHEAD
Kudos are welcome...
0 Kudos
Message 2 of 3
(4,189 Views)
Hello, I have an error code of 62 when linking S7-200.
Ask for help! ! ! It's very urgent!

0 Kudos
Message 3 of 3
(3,879 Views)