I have a NI 9477 DO module to control valves in our setup. Some of them require 12VDC and some 24VDC power supply input. Can I control these using the same card? If yes, how will I make the common separate for both the voltages? 

Thank you in advance.

0 Kudos
Message 1 of 3
(1,158 Views)
Solution
Accepted by topic author Agupta25

Unfortunately, it looks like all the channels share the COM pin and you cannot have isolated COM for the channels.

 

For the voltage question, you can go up to 60V @ 1A max per channel.

 

If you are not concerned about common ground for 12V and 24V, each channel can control loads at different voltages given it is an open collector type connection.

Santhosh
Soliton Technologies

New to the forum? Please read community guidelines and how to ask smart questions

Only two ways to appreciate someone who spent their free time to reply/answer your question - give them Kudos or mark their reply as the answer/solution.

Finding it hard to source NI hardware? Try NI Trading Post
0 Kudos
Message 2 of 3
(1,121 Views)

Thank you. I will try connecting through an open collector-type connection.