I have been trying to use a 1804 network module with a AIO-610, this has been working fine so far with firmware 6.08 (tried 6.05 but no improvement) I can write AO channels in max and via modbus however when I try and read the AI channels (using voltage 0-36V range and a 24V hardwired voltage input) the reading in max remains floating. Is this a firmware/compatabilty issue or am I doing something wrong? I have swapped the module for a known working unit and the same issue arises.
I am using LV 2015.
02-23-2016 04:04 AM
Hello DQIS,
What do you mean by 'Remains floating'?
Secondy you said that the same issue arrises with a known to be working module, what wwas the setup that the known module worked in?
Did you try to test the module AIO-610 in the working setup?
Best regards,
Guy
02-29-2016 02:42 AM - edited 02-29-2016 02:47 AM
Hello DQIS,
What did you connect to the input, a known signal with 24V DC or AC?
And is it the device grounded?
Best regards,
Guy
03-07-2016 08:10 AM
The device was grounded and the test signal was 24VDC, the fault was traced to the IAK having each logical channel mapped to the fourth (unused and floating) physical channel. It worked fine once we had realised what we had done.