10-04-2016 08:34 AM
I am getting a CRC/LRC error from a half duplexed 485 system connected to a Watlow controller. I have the instrument configured in MAX for 4-wire auto and I have this code running on other identicle systems with out an issue. Does anyone have an idea as to what would cause such an error?
Solved! Go to Solution.
10-05-2016 02:00 AM
In most cases I know a 485 connection is a 2 wire connection. Maybe you should set MAX to 2-wire auto.
Kees
10-05-2016 06:27 AM
That would be good to try but unfortunatley MAX has that section greyed out and I cannot change it and am not sure how to get MAX to let me. Do you know why MAX has that greyed out?
10-06-2016 01:52 AM
I think it depends on the kind of interface you are using. Is it from NI or ?
10-12-2016 06:35 AM
It turns out that the reason for it being greyed out was to change the advanced functions you must logon to MAX as admistrater. Once I had access I changed the 4-wire to 2-wire auto and the system worked fine.