Communication Protocol with RS485 and Yokogawa UP351

Here are the images you requested.
Download All
0 Kudos
Message 11 of 22
(3,253 Views)
Thank you for the images. I tried the same but it is still not working. I am getting a byte count of 0 for the Bytes at Port.
I have attached a screenshot of the vi.
0 Kudos
Message 12 of 22
(3,247 Views)

Have you tried communicating with this using another software package to verify that your port and cabling is correct?

Which communications format are you using?  PC Link or Modbus?

What command are you trying to execute?

What is the actual string you are writing via the VISA write?

0 Kudos
Message 13 of 22
(3,240 Views)
Communicating via the LL100 software works fine. I am using PC Link.
I am using the same command \0201010INF6\03\r
When I hardwire 6 as the bytecount, the visa read operation times out
0 Kudos
Message 14 of 22
(3,233 Views)
Are you sure that your string control on the front panel is set for "\" display?
0 Kudos
Message 15 of 22
(3,222 Views)

i did not understand your question
how do i set it?

Message Edited by arbit on 08-02-2007 01:16 PM

0 Kudos
Message 16 of 22
(3,222 Views)

Some of the characters you need to send to the controller are "non-displayable" in a normal string control/indicator.  If you right click your front panel string control a drop down menu will appear.  One of the options is "\" display. 

See this for more info.  http://zone.ni.com/reference/en-XX/help/371361B-01/lvhowto/backslash_codes_display/

Message 17 of 22
(3,215 Views)
Thanks a lot. It works now!!!!
0 Kudos
Message 18 of 22
(3,210 Views)
Thank you very much for your insightful and patient help.
0 Kudos
Message 19 of 22
(3,208 Views)
You are most welcome and thanks for letting me know you got it working.  Smiley Happy
0 Kudos
Message 20 of 22
(3,203 Views)