03-07-2016 11:20 AM
You will have to get DriveWindows Light from your ABB distributor. More than likely, you don't have all the drive parameters set correctly.
03-07-2016 11:50 AM
HIghland,
Whatever image you have in your signature is not showing up. It says it points to your gallery, but according your gallery, it is "hidden".
03-07-2016 11:59 AM
Yeah, I know. I need to fix that. It is supposed to be the CLD logo.
03-07-2016 12:05 PM
So i just contacted ABB tech support and they told me the Drive Window lite is only serial based. So i cant test my network with it. He said it would help with backing up the configuration and pushing it back to multiple units. But i only have 3 VFDs.
And as expected i get same information. send 1150 (stop) and 1151 (start) to address 40001, which i read as address 0 in the modbus api. then 40002 is for the frequency speed control location.
Also told me to set param 1001 and 1103 to COMM. but i think i have that already, ill need to check again.
Man i bet this is just one stupid parameter not set right. WHY MODBUS! so many parameters!!!
03-07-2016 12:07 PM
Use, DWL is for configuration. It makes it easy to look at parameters and save them to a file so someone else can look at your settings. All of your data may be going just fine to the Fieldbus parameters, but if the drive isn't told to use them, then it won't work.
03-07-2016 12:16 PM
Testing my CLD logo....
03-07-2016 12:21 PM
Looks like the HTML is pointing to your public library now. But it gets cut short there. It isn't pointing all the way to the image.
03-07-2016 12:22 PM
How about now?
03-07-2016 12:23 PM
Finally.
03-07-2016 12:23 PM
Crap. That is the CLAD logo, not the CLD. OK, will fix it.