HI Bob,
Thank you for posting the VI's for us to look at!
A couple of notes:
1) On the recieving side, use one TCP/IP read to get the byte count, then use that value to control how many bytes ared in the the second TCP/IP read.
2) Your byte count will be 4 bytes not 3
3) Sent the byte count as a seperate TCP/IP packet. Do not concantentate the two.
4) Last I looked, property nodes did NOT work in a deplyed LV 6.1 RT app.
5) Global variables are OK if they are written only one place. Is that statement true for all of your globals?
I hope this helps,
Ben