09-17-2024 02:45 AM
Hola a tod@s, tengo el siguiente pgm intentando leer un equipo slave en modbus.
He comprobado el UnitID, starting adress y el number de holding register, es el correcto.
Pero al ejecutar me da el siguiente error:
SubVIs.lvlib:RTU Data Unit.lvclass:Read ADU Packet.vi:5030001
Alguna idea porqué me ocurre?
Gracias
Solved! Go to Solution.
09-17-2024 06:45 PM
@qrm77 wrote:
Hello everyone, I have the following pgm trying to read a slave device in modbus.
I have checked the UnitID, starting address and the holding register number, they are correct.
qrm77_0-1726558794046.png
But when I run it I get the following error:
SubVIs.lvlib:RTU Data Unit.lvclass:Read ADU Packet.vi:5030001
Error 56 is a generic timeout error. The master didn't get any response from the slave.
Try to run NI I/O Trace and see if the slave responses with any message. You can compare the result from a different master, like QModMaster
09-18-2024 02:45 AM
Thank you very much Kudos!! I'll try it.