You can go to automationdirect.com/cmore but the communication is simply Modicon Modbus. Please see my original post for attachments of how the CMore is set up. It's Modbus addressing, TCP/IP set up.
Thanks,
Teri
0 Kudos
Message 11 of 19
(1,787 Views)
 
 
 

Are you using a crossover ethernet cable to connect directly to the pc from the Cmore?? Or do you have a switch/hub in between with straight thru cables. See page 1-13.

http://web2.automationdirect.com/static/manuals/eauserm/ch1.pdf

See page 5-32,33 for testing plc communication.

http://web2.automationdirect.com/static/manuals/eauserm/ch5.pdf

After reading the modbus info again, the CMORE panel should be the master and initiate all of the communication. The PXI unit should act like a modbus slave.

https://knowledge.ni.com/KnowledgeArticleDetails?id=kA03q000000YFZOCA4&l=en-US



Message Edited by unclebump on 01-23-2008 05:58 PM

Message Edited by unclebump on 01-23-2008 06:01 PM

0 Kudos
Message 12 of 19
(1,773 Views)

The first thing i would recomend is get it talking outside of labview thru something like modscan just to verify you have the connectivity.

 

-Tim C.

1:30 Seconds ARRRGHHH!!!! I want my popcorn NOW! Isn't there anything faster than a microwave!
0 Kudos
Message 13 of 19
(1,762 Views)
I finally got it all to work! I had an address setting in the CMore set incorrectly...stupid, but it happens, usually to me! I was going back and forth in the Automation Direct forum, trying free modbus simulators and one gentlemen had me painstakingly go through all my settings. I probably wouldn't have caught it for awhile since I'm constantly being pulled in different directions! We all know how that is.

Thanks to all for the help.

Teri
0 Kudos
Message 14 of 19
(1,751 Views)
Remeber, you may need to verify the register offset to ensure you are reading the right register.  For example the equipment documentation may list register 4000 as a certain value but when LV reads it with a setting of 4000 you may be reading 3999 or 4001 ( I get it confused). 
 
Best Regards
-Tim C.
1:30 Seconds ARRRGHHH!!!! I want my popcorn NOW! Isn't there anything faster than a microwave!
0 Kudos
Message 15 of 19
(1,739 Views)
Thanks Tim, I'll keep that in mind. Now on to my next problem...reading CAN messages into the PXI system using a hand-held device...I got stuck on that the other day. Hopefully I'm doing something just as stupid as the the last problem!
Teri
0 Kudos
Message 16 of 19
(1,728 Views)

If at all possible could you show an example of communicating between labview and CMore?

Read and write to and from.

 

 

Thanks

0 Kudos
Message 17 of 19
(787 Views)

Is there any way you could post an VI on how you connected to cmore screen with labview? Thank you.

0 Kudos
Message 18 of 19
(432 Views)

The thread is more than 15 years old and you queried it already 4 years ago with no reaction.

Rolf Kalbermatter
My Blog
0 Kudos
Message 19 of 19
(422 Views)