02-23-2023 03:01 PM
That seems to be the correct way. My apologies.
03-03-2023 06:59 AM
Do you mean that I should switch back and forth between the addresses? Read one, change address, read the next?
Thanks!
03-03-2023 09:24 AM
Yes, exactly. In principle, you can also set the unit ID once and create an array of Modbus Master instances.
12-04-2023 03:33 PM
@StevenD escreveu:
I think I have used two devices on the same COM port. The NI Modbus Library should be smart enough to deal with it as multidrop is part of the Modbus specification (assuming it is 485 wiring, not 232). If you do have issues with it, there is another Modbus Library other people on the forums use called Plasmionique
https://www.vipm.io/package/mb_master/
Are you aware if this is true for slaves too?
For example, multiple LabVIEW modbus slaves in the same COM port?
Regards,