Helo Guys currently Im working in overhauling old training modules, but I have hit a brick wall the problem that Im having is that I currently im working with a flow sensor that creates pulses depending on the flow of the liquid, the problem that im having is that currently im using a CDAQ 9174, with analog module during my research I found that this model DAQ9174 doesnt allow for counters, and decided to use analog input to measure but no sucess do you guys have any ideas
09-23-2015 01:14 AM
Hi Javier,
where did you read that the 9174 doesn't have counters on board? It has 4 of them and you can use them to create a pulse counter based on that with basically any DI module that has a fast enough front end.
Even with an AI you should be able to implement a pulse counter: Just take measurements and compare to a threshold value to detect rising edge, then increment. Where exactly is your brick wall?