NI-Sync IEE1588v2 does not sync cRIO System Time

I have a PXI 6682 with NI-Sync 3.1 and have verified a good GPS IEEE1588 master clock on the PC.

I have loaded the NI-SYNC Pioneer on my cRIO but cannot see any sort of time sync.  Also

a IEEE1588 property called clock state is reading 'faulty'.  The only evidence that anything has changed on my

cRIO is that now timed loops are not syncing to the scan engine.  I had to change scan sync'd timed loops to fixed 

iteration times to get my rt app running again.  Has anyone had any luck with the NI-SYNC pioneer software?

 

0 Kudos
Message 1 of 4
(3,710 Views)
What cRIO are you using?
0 Kudos
Message 2 of 4
(3,701 Views)

I have two cRIO-9074 chassis each with a 9144 EtherCat expansion chassis.

 

0 Kudos
Message 3 of 4
(3,697 Views)

Is your system using a Link-local IP? If so, the Beta 2 of the SW Sync pioneer will support waiting for the IP to come up before going faulty (Link Local IP may take up to 60 seconds). Note that Beta 2 of the SW Sync which isn't up on the web yet (though we could provide it to you) only supports the LabVIEW 2009 platform beta.

 

Thanks

0 Kudos
Message 4 of 4