Hello Bryan,
In your case, if you are using an SCXI module to connect to your signals for your six measurement tasks, it might be the sampling rate of the SCXI module that is the limiting factor. Are you using an SCXI module to connect to your signals? If so, what are the model numbers of both the SCXI chassis and module?
Best wishes,
Wallace F.
07-07-2008 11:13 AM
07-08-2008 06:02 PM
Hello Bryan,
The scan rate of your data acquisition setup is dependent on four things:
1. The sampling rate of your DAQ board.
2. The sampling rate of the slowest SCXI module.
3. The number of channels in your scan list.
4. The resolution of your DAQ board.
In your case, the SCXI-1102s sample at 333kS/sec while the PCI-6036E has a sampling rate of 200kS/sec. That means that to start with, your limiting aggregate sampling rate is going to be 200kS/sec. Now take into account the number of channels in your scan list by dividing the sampling rate by 6 to get 33.33kS/sec. When you take into account the minimum settling time required by you SCXI modules for a 16 bit resolution DAQ board, and this will reduce that 33.33kS/sec/channel quite significantly. In fact, the settling time required for a 16 bit DAQ board will reduce an aggregate sampling rate of 333kS/sec to an aggregate sampling rate of 50kS/sec. When you divide this by 6, you get approximately 8kS/sec/channel. Consider how much less this would be if you started with an aggregate sampling rate 0f 200 kS/sec instead of the 333kS/sec. For more information, please reference the knowledgbase article linked below.
http://digital.ni.com/public.nsf/allkb/410A70C25A4D12B486256A1E0070BDAE?OpenDocument
Best wishes,
Wallace F.