12-07-2007 08:00 AM
12-10-2007 12:31 PM
Hi Atakahas,
Unfortunately we don’t have any differential to TTL (single ended) signal conditioning card, and since you will probably end up building the circuit it will be better to get a custom DIN rail box. For reference I can point you to this knowledgebase: where gives you a suggestion on how to build the circuit: How Can I Connect a Differential Encoder to a PCI/PXI-660x?.
All the products that I have found on ni.com for DIN-Rail Accessories are for our own cards like USB devices, TBX connector blocks, etc not for a custom DIN rail that you will probably end up building.
I hope it helps
12-10-2007 01:18 PM
12-11-2007 11:14 AM - edited 12-11-2007 11:14 AM
Hi Atakahas,
I was researching if future 660x models will have differential inputs and it seems that not, at least in any time soon. What I will suggest is: “Product Feedback” and I can ensure you that our Research and Development department really takes a look at this suggestion; so making the suggestion would be the right course of action to take.
06-17-2009 11:50 AM
I saw this KB http://digital.ni.com/public.nsf/allkb/B3945A72AE53D1B086256EF7007C4D0D
If my encoder is differential output. Which means it has A+,A-,B+,B-,
According to this KB. I can connect A+B+ and A-B- to different counter to get better accuracy(differential input).
But I can't find any setting that allow me to bind the two channel together. Or it means if I wire like this. The 660x card will automatically treat the encoder as differential input?
Ethan
07-21-2009 06:26 PM
08-13-2009 11:39 AM
08-14-2009 10:04 AM
08-17-2009 12:13 PM
The optical isolator module acts as a buffer to convert the differential encoder signal to single ended. It does not effect the resolution.
Here is a link to the optical isolator user guide from the BEI web site:
http://www.beiied.com/PDFs2/oim.pdf
Use the diagram in Connection Instructions #1 with the differential output encoder. Connect A, B, Z and common to the NI module. Do not connect module outputs A/, B/ or Z/ (they float).