10-15-2012 10:55 AM
Hello everyone. I must connect a pressure transducer with 5 pin output
and i have a rj50 pin DAQ device NI 9237, so i must connect pins (2 to 2) (3 to 3) (6 to 1) and (7 to 4) according to the datasheet:
Can i start to test my device in the test panel after i making these connections ?, or is there anything else i must be aware of ?
10-17-2012 03:52 AM
Hi Oesen
Have you figured this out yet? If not I will be more than happy to assist you.
Best Regards
Anders Rohde
Applications Engineer
National Instruments Denmark
10-17-2012 07:26 AM
Thanks for the reply.
No.. I will connect it within few hours, but i'm not sure about the procedure. Is there anyting else i should do ?.
10-17-2012 08:28 AM
Hi Oesen,
What Pressure Transducer is it? Is it a half bridge, full bridge or quater bridge?
Best Regards
Anders Rohde
Applications Engineer
National Instruments Denmark
10-18-2012 08:18 AM
No idea. I have written to Edwards.com and they didn't answer me.
It is this one:
http://www.edwards.com/products/pressuremonitoring/pages/truwave.aspx
10-18-2012 09:54 AM
Hi Oesen,
Thanks for you reply, I will need to see the datasheet for the transducer so I can see this information. Normally I would expect some resistance (R+ and R-) to be wired to the 9237 as well.
Best Regards
Anders Rohde
10-18-2012 02:38 PM
Hi Anders
I have got an answer from Edwards:
Yes, all of Edwards transducers use full “Wheatstone” bridge technology on the silicone chip with additional temperature compensation circuitry contained on the ceramic mounting substrate.
They have only 5 pins output, so i dont think there are any resistive pins.
10-18-2012 04:06 PM
Hi Oesen
Then it looks like a full bridge configuration from his answer. It then looks correct what you have drawn. Note that you might need to configure the resistance in the software to get correct reading. See below cut out and reference::
----------------------------------
When working with the NI 9237, there are three possible configurations:
----------------------------------
Why is there No Nominal Resistance Specification for NI 9237?
http://digital.ni.com/public.nsf/allkb/4E6C5E0B1FE562E6862576370006BFA1?OpenDocument
If you are trying to verify the reading the please remember that the 9237 will output in V/V and not in V see below reference:
Incorrect Voltage Readings on the NI 9237
http://digital.ni.com/public.nsf/allkb/21CA039D8F43C5188625729F005AC2F7?OpenDocument
Hope this helps you in the right direction.
Best Regards
Anders Rohde
Applications Engineer
National Instruments Denmark
12-06-2013 08:14 AM
Hi,
did you manage to read pressure from the sensor?
I am trying to acquire the signal using a 6009 but still doesn't work!
Leonardo
12-06-2013 04:31 PM
Hi wonderblock.
Yes it worked.