Hello,
Can the I/O Server use Modbus Function Code 16 (preset/write multiple holding registers)? Essentially, my CompactRIO needs to send a 48-bit integer to a slave device, which means I need to write 3 registers.
I found a way to do it without I/O Server (http://zone.ni.com/reference/en-XX/help/370622M-01/lvmve/modbus_master_write_read_multiple_holding_r... ), but I was wondering if I could do the same using I/O Server.
Thanks!
Solved! Go to Solution.
08-03-2015 04:02 PM
Hello JKSH,
Unfortunately, a bound shared variable cannot read\write from 3 registers at once automatically. Below is a document which details Modbus I\O Server bound shared variable capabilities.
Using Modbus I/O Servers (DSC Module or Real-Time Module)
http://zone.ni.com/reference/en-XX/help/371618G-01/lvmve/dsc_modbus_using/
You do have the option to access two adjacent 16-bit input registers as one 32-bit shared variable but not 48-bit.
Regards,
j_bou