09-09-2015 10:07 AM
I Have several ML1000's connect to a DH485 network by 1761-NET-AIC modules. RSLogix can communicate with each using 1747_PIC / AIC+ driver on a Windows XP SP2 or older computer. Is there a driver for NI OPC server 2012 that will communicate with all of the ML1000 nodes on the DH? DF1 and DH+ drivers do not work.
09-10-2015 12:05 PM
Hey tmckeown,
I'm guessing that the ControlLogix driver will also not work since it uses 1761-NET-ENI for communication. Is that correct?
09-10-2015 12:20 PM
Correct. I am going to try the 1747-UIC USB to DH485 converter cable with the DF1 driver. Cable is ordered waiting for it to arive.
09-10-2015 01:07 PM
I believe that would be the best way to go! Let me know if you have any questions after you get it!
10-02-2015 05:33 AM
Tested the 1747-UIC cable and it work for my application. Thanks.