Hi all,

 

I am trying to create a LabVIEW controller for something that I was recently doing with an Omega temperature controller. The task is this:

 

Create a simple on/off controller for a heater based on a user-provided temperature setpoint. The physical system consists of a thermocouple, a solid state relay for the on/off control, and a cartridge heater. 

 

My thought is that I can replace my previous controller with a DAQ, but I am just not sure how to proceed. I can set up the DAQ system to record temperature from the thermocouple, but I get stuck on how to combine that with the SSR and the temperature setpoint. 

 

Theoretically I would compare current temperature reading from the thermocouple with the temperature setpoint. If temp < setpoint, then the DAQ would output a 5 V signal to the SSR which would activate and close the relay (heater on). If temp > setpoint, then the DAQ would not output anything and the SSR would be open (heater off). 

 

Physically, I would connect the thermocouple to the DAQ input channels and the SSR wires to the Digital I/O channel. 

 

Can anyone help me with this? I can provide more information or a drawing if necessary. Thank you!

0 Kudos
Message 1 of 4
(766 Views)

You can do it but think twice if this is what you want.

 

Imagine what would happen if your computer hangs due to a virus or a windows update and the heater is stuck at ON?

 

Anything that results in catastrophic failure must be hardware controlled and safe guarded instead of through a software.

Santhosh
Soliton Technologies

New to the forum? Please read community guidelines and how to ask smart questions

Only two ways to appreciate someone who spent their free time to reply/answer your question - give them Kudos or mark their reply as the answer/solution.

Finding it hard to source NI hardware? Try NI Trading Post
0 Kudos
Message 2 of 4
(748 Views)

Hi Santhosh,

 

This isn't a high-risk operation and currently I can simply unplug my heater, or include a remote emergency stop button. I understand that it can be done, but I am more looking for guidance on a way to implement this (namely, at this point, the proper way to output my 5V signal from a DAQ at one condition and no signal at the other).


Thanks,

Natalia

0 Kudos
Message 3 of 4
(742 Views)

Hi nkn,

 


nkn5110@psu.edu wrote:

I am more looking for guidance on a way to implement this (namely, at this point, the proper way to output my 5V signal from a DAQ at one condition and no signal at the other).


Please rethink your wording!

You don't want to output "no signal" in the "other case", but you want to output 0V!

 

So your problem reduces to use a Select function to select between 5 and 0 (regarding TRUE/FALSE condition) to output on your AO channel…

Best regards,
GerdW