Multifunction DAQ
Connecting a Veris Differential Pressure Sensor PXU to NI 6008
I want to connect a Veris Industries Differential Pressure Transmitter Model PXULX05S to a National Instrument NI-6008.  I’m not sure of the wiring setup from the PXU to the NI-6008.
It is a 3 wire configuration.  Measurement type voltage 0-10v raw.  The scaled value will be 0-10 in. w.c.  I have a 24vdc power supply connected to the PXU unit.
How should I connect from the PXU to the NI 6008?
(3,530 Views)
Can you post the link to the manual for this device? Also is this a bridge based transducer?
Carl W.
Applications Engineering
(3,516 Views)
Thank you for your response.
The sensor uses a ceramic capacitive pressure transducer with a frequency output.
I have attached a installation guide.
(3,504 Views)
Accepted by topic author Bigblue239
It looks like in Voltage mode you would hook up the out to an analog input channel on the 6008. Then the com to a ground on the 6008. The power comes from a power supply and make sure you are including this in your ground as the document lays out.
Carl W.
(3,480 Views)
Thanks for the help.
(3,471 Views)