05-28-2013 02:41 PM
I want to connect a Veris Industries Differential Pressure Transmitter Model PXULX05S to a National Instrument NI-6008. I’m not sure of the wiring setup from the PXU to the NI-6008.
It is a 3 wire configuration. Measurement type voltage 0-10v raw. The scaled value will be 0-10 in. w.c. I have a 24vdc power supply connected to the PXU unit.
How should I connect from the PXU to the NI 6008?
Solved! Go to Solution.
05-29-2013 09:23 AM
Can you post the link to the manual for this device? Also is this a bridge based transducer?
05-29-2013 02:12 PM
Thank you for your response.
The sensor uses a ceramic capacitive pressure transducer with a frequency output.
I have attached a installation guide.
05-30-2013 01:14 PM
It looks like in Voltage mode you would hook up the out to an analog input channel on the 6008. Then the com to a ground on the 6008. The power comes from a power supply and make sure you are including this in your ground as the document lays out.
05-30-2013 01:22 PM
Thanks for the help.