12-13-2016 10:42 AM
Hi,
a quick question: Is it possible to use the PFI0 on cDAQ 9132 as a readable Digital input, instead of a timing source/trigger?
12-14-2016 05:45 AM
Hi fredlaks,
I had a look in the reference manual for the cDAQ 9132 (http://www.ni.com/pdf/manuals/371801b.pdf) and under the 'Module PFI Characteristics' on page 6, the manual states:
"Functionality: Static digital input, static digital output, timing input, and timing output"
So I would assume that this means it is possible.
I have attempted to simulate the cDAQ 9132 device but I was unable to target the PFI line as a static digital line.
I believe this is because the option is only available when running the RTOS. As I don't have the hardware I am unable to confirm my suspicion, but hopes this at least clarifies the situation for you.
Kind Regards,
Nathan Smith
I hope thi
12-14-2016 06:07 AM - edited 12-14-2016 06:11 AM
Thanks for the reply.
I am using the RTOS
I have been trying a bit today, and i am also unable to target the PFI0 when setting up a DI channel.
I tried another approach by setting up the PFI0 as input to one of the internal counters in the cDAQ. Now i can access the PFI0, but i cannot access the counter. The internal counters simply doesn't appear as a selectable resource.
I am using a very simple example to test with at the moment. The example is for cDAQ 9178, but i would assume that the process to set up a PFI0 edge counter would be identical on 9132.
The route between PFI0 and Counter0-3 mappears green in MAX (under cDAQ->Device routes), so it should be possible to use the PFI0 as input to counters. Is there anything i am missing, do i have to enable the counters somewhere or something? I am quite new to the cDAQ, btw.
12-15-2016 03:53 AM
Hi fredlaks,
I've had another look into this and attempted to do the same thing with a differnt cDAQ chassis. I don't believe this is possible.
I think the information I eluded to in my previous message is actually referring to routing the pfi line to a module and not the controller. The extract I quoted to you was under the 'Module PFI Characteristics' heading and not under the 'Controller PFI Characteristics' heading.
Hope you manage to solve your issues some alturnative way.