Hello,
I'm tring to program a PXI-7841R. It is mounted on a PXIe-1085 and is connected to a SCB-68A.
I'm trying to read the analog output channels with my multimeter but i'm always reading 0 even though the channels seems to be "activated". Their impedance is low.
The DO are working fine, thus I think i'm missing something trivial but I can't figure out what. I'm new with labview. I'll attach a printscreen of my test program.
Thank you for your help.
Solved! Go to Solution.
06-22-2016 05:13 AM