A510 VFD Modbus RTU via RS485_DI state values in register
I have a Teco Westinghouse A510 VFD which i am controlling a 3phase motor/hoist and I am controlling using the Modbus Library via RS-485 and using serial com RTU.
I am getting the motor to spin and write to the registers, however, I am having difficulty reading a particular register with multiple bits that I need to access on the same register, see the images below (Modbus Com manual for VFD). I have uploaded my vi below and also the modbus manual for the VFD for reference.
I need to access the DI state to read if they are open (0) or closed (1). Also, does the Modbus API control the CRC check or do I need to include that somehow, if so how?
Any help would be greatly appreciated.
(945 Views)
Accepted by ikhan123
Read the register 2522H. It should return a U16. Then convert the U16 to Boolean array.
Modbus Library will handle the CRC.
Control Lead | Intelline Inc
(913 Views)
Hi ZYOng,
much appreciated.
Thanks.
(887 Views)
I also want to write to a register with multiple bits as in the above example but instead of reading a list of booleans, how would I write-to or read non-boolean from a sub-register?
Please see the figure below, how would I write to register to 2501H bit F to turn the Torque command set by Communication: ON
Thanks for any help and support.
(879 Views)
(870 Views)
Bit F is the 15th bit (using 0-indexing).
Similarly you can use Boolean Array to Number to get the U16 value.
(863 Views)
thanks, it worked!
(847 Views)