LabVIEW

cancel
Showing results for 
Search instead for 
Did you mean: 

A510 VFD Modbus RTU via RS485_DI state values in register

Solved!
Go to solution

Hi,

 

I have a Teco Westinghouse A510 VFD which i am controlling a 3phase motor/hoist and I am controlling using the Modbus Library via RS-485 and using serial com RTU.

 

I am getting the motor to spin and write to the registers, however, I am having difficulty reading a particular register with multiple bits that I need to access on the same register, see the images below (Modbus Com manual for VFD). I have uploaded my vi below and also the modbus manual for the VFD for reference. 

 

I need to access the DI state to read if they are open (0) or closed (1). Also, does the Modbus API control the CRC check or do I need to include that somehow, if so how?

 

Any help would be greatly appreciated.

 

 

Thanks,

ikhan123_0-1718891214477.pngikhan123_1-1718891280676.png

 

Download All
0 Kudos
Message 1 of 7
(897 Views)
Solution
Accepted by topic author ikhan123

Read the register 2522H. It should return a U16. Then convert the U16 to Boolean array.

ZYOng_0-1718930269266.png

 

Modbus Library will handle the CRC.

 

-------------------------------------------------------
Control Lead | Intelline Inc
Message 2 of 7
(865 Views)

Hi ZYOng,

 

much appreciated.

 

Thanks.

0 Kudos
Message 3 of 7
(839 Views)

Hi,

 

I also want to write to a register with multiple bits as in the above example but instead of reading a list of booleans, how would I write-to or read non-boolean from a sub-register?

 

Please see the figure below, how would I write to register to 2501H bit F to turn the Torque command set by Communication: ON

 

ikhan123_0-1719434430751.png

 

Thanks for any help and support.

 

Regards,

 

0 Kudos
Message 4 of 7
(831 Views)

Hi,

 

I also want to write to a register with multiple bits as in the above example but instead of reading a list of booleans, how would I write-to or read non-boolean from a sub-register?

 

Please see the figure below, how would I write to register to 2501H bit F to turn the Torque command set by Communication: ON

 

 

ikhan123_1-1719446249968.png

 

 

Thanks for any help and support.

 

Regards,

0 Kudos
Message 5 of 7
(822 Views)

Bit F is the 15th bit (using 0-indexing).

Similarly you can use Boolean Array to Number to get the U16 value.

ZYOng_0-1719449258949.png

 

-------------------------------------------------------
Control Lead | Intelline Inc
Message 6 of 7
(815 Views)

thanks, it worked! 

0 Kudos
Message 7 of 7
(799 Views)