Converting modbus hex-data from one register into float
I have different settings for the range here that i can readout:
Solved now with your calculation:
-10V..+10V --> Range=10
-5V..+5V --> Range=5
-1V..+1V --> Range=1
-500mV..+500mV --> Range=0.5
-150mV..+150mV --> Range=0.15
But what to do with:
4mA..20mA
-10mA..20mA
0mA..20mA
-210°C..760°C
270°C..1372°C
can the calculation be changed to accept two values?
Thx again.
Message 11 of 18
(1,385 Views)
Accepted by OnlyOne
Try this out:
GCentral
Message 12 of 18
(1,381 Views)
Hm, found a problem...the given Read- value is a U16 and not  an I16.
What do i have to change?
Thank you
Message 13 of 18
(1,361 Views)
Thank you
Are you sure about that?  That would not work for the -10V to +10V range.  Possibly for the temperature one.  In that case, you just need to add by the minimum value instead of the average of the max and min.
GCentral
Message 14 of 18
(1,351 Views)
I am sure because the open-source modbus-dll that provides the function to read out this register returns an ushort-array.
Here are some values that are displayed in the webinterface for +/- 10V-range:
FFFC = -0,001
F32D = -1,001
E662 = -2,001
BFF7 = -5,001
8CB8 = -9,006
8000 = -10V
0005 = 0,001
0CD3 = 1,001
199E = 2,001
4008 = 5,003
7340 = 9,006
7FFF = 10V
So it looks like 0V..10V is displayed as 0005x to 7FFFx
and
the negative values are 8000x to FFFFx in opposite order.
But how to put this in a vi including the different ranges?
Message 15 of 18
(1,344 Views)
FFFC = -0,001
F32D = -1,001
E662 = -2,001
BFF7 = -5,001
8CB8 = -9,006
8000 = -10V
0005 = 0,001
0CD3 = 1,001
199E = 2,001
4008 = 5,003
7340 = 9,006
7FFF = 10V
and
It is actually using 2's Complement.  By definition, that is an I16.
GCentral
Message 16 of 18
(1,339 Views)
Thx -
Now, after everything is working, i found in the module an option to set the return-value to Engeneering-format 🙂
Message 17 of 18
(1,332 Views)
@OnlyOne wrote:
Thx -
Well, I hope you at least learned something through this experience.
GCentral
Message 18 of 18
(1,327 Views)