What is the make and model of the device you are trying to communicate with using Modbus?

========================
=== Engineer Ambiguously ===
========================
0 Kudos
Message 12 of 15
(128 Views)

The issue has been resolved.
Changing the mode on both ends from ASCII to RTU solved the problem.

0 Kudos
Message 13 of 15
(124 Views)

I swear I mentioned that... 

 

@RTSLVU wrote:

Have you tried serial type RTU? 


Anyway I'm no Modbus expert but to be honest I have never seen a Modbus device that used ASCII mode.

========================
=== Engineer Ambiguously ===
========================
0 Kudos
Message 14 of 15
(117 Views)
 

Yes, you mentioned it earlier, but the device manual explicitly states that "Modbus serial RTU and ASCII are supported." That's why I decided to try using ASCII. However, I still can't figure out why ASCII isn't working while RTU works perfectly fine.

0 Kudos
Message 15 of 15
(89 Views)