12-20-2024 11:16 PM
yes
12-26-2024 09:07 AM
What is the make and model of the device you are trying to communicate with using Modbus?
12-26-2024 09:16 AM
The issue has been resolved.
Changing the mode on both ends from ASCII to RTU solved the problem.
12-26-2024 09:53 AM
I swear I mentioned that...
@RTSLVU wrote:
Have you tried serial type RTU?
Anyway I'm no Modbus expert but to be honest I have never seen a Modbus device that used ASCII mode.
12-28-2024 12:17 AM
Yes, you mentioned it earlier, but the device manual explicitly states that "Modbus serial RTU and ASCII are supported." That's why I decided to try using ASCII. However, I still can't figure out why ASCII isn't working while RTU works perfectly fine.