Date rates of 200Hz are a bit high for typical OPC server.
You may want to poke around with the OPC server settings to see if you can bump up the update rate but you are definitely pushing it.
100 Hz is the highest I would depend on an OPC interface.
An aside...
LabVIEW Channel wires come in multiple flavors including a Tag type. The Tag flavor offers the most recent update and are lossy. It is no accident NI chose the name "Tag" since that is what OPC servers and PLCs expose.
Take care,
Ben
12-11-2019 09:26 AM
12-11-2019 09:34 AM
@Ben ha scritto:
Date rates of 200Hz are a bit high for typical OPC server.
Actually it's 20 Hz. Not a rate I'm experienced about, anyway.
12-11-2019 09:38 AM
You are correct Paolo!
My bad.
I can not say what the top update rate can be.
OPC is generally used for slow changing values and checking what the value is NOW.
Ben