I have multiple cRIO-9081. Each cRIO-9081 is running NI-DAQmx 15.5. On four of the cRIO-9018 we have attached cDAQ-9178s with 8 modules. Everything just worked. On the fifth cRIO-9018 we attempted to connect a cDAQ-9174. The device showed up in MAX and Windows Device Manager, but MAX reported that the device was not present (Error -88705) and that Windows did not find a driver for the instrument.
We then plugged in a cDAQ-9178 into the fifth cRIO and everything just worked.
What is the difference between a cDAQ-9174 and a cDAQ-9178 other than the number of module supported?
Paul
Solved! Go to Solution.
06-17-2016 06:17 PM
Hi Paul,
In terms of specifications, the two cDAQ chassis should have almost exactly the same specs (at least in all the ways that would affect that connection) -- the only main difference is the number of modules, as you mentioned. More detail on the specs can be found here:
http://www.ni.com/datasheet/pdf/en/ds-178
http://www.ni.com/pdf/manuals/374045a.pdf
http://sine.ni.com/nips/cds/view/p/lang/en/nid/207534
It looks like something may be wrong with your 9174 -- is it working when connected to another system? These are also some great troubleshooting steps to start with: http://digital.ni.com/public.nsf/allkb/34CC88F4838CD37E86256A290066A2BE
06-19-2016 08:18 AM
Sunayna,
Yes the 9174 works with other computers.
Paul
06-21-2016 04:38 PM
Hi Paul,
This seems like it may be a driver issue! What version of DAQmx do you have installed on both computers? A reinstall of the newest version might be worth a shot since it looks like there may be some corruption. You can find the newest version here: http://www.ni.com/download/ni-daqmx-15.5/5901/en/
You can also manually associate the driver with the device, here: http://digital.ni.com/public.nsf/allkb/5B80CAAA64413B4C86256C5E0000C1A7
Are there any modules plugged into the cDAQ chassis?
Also, sometimes this can happen if you do not reboot your computer after installing NI-DAQmx. Rebooting your computer after installing the driver will allow you to reserve the device successfully. Here are a few other steps to try:
06-22-2016 07:25 AM
Sunayna,
Reloading NI-DAQmx 15.5 and resetting MAX configuration database fixed the issue.
Paul